fineartsnyc
Mechanical
- Dec 19, 2011
- 22
NYC climate. 95 DB and 74 WB Outdoor Temp.
we have a Mitsubishi Citi multi R-2 Series (heat recovery system) with BC controller, sub controller and (Lossnay) ERV system on the upper floor
3 fire places with FA.
Fresh air is introduced to the space thru the ERV system (as designed). I was told by the MC that the ERV is off.
One exhaust fan for 6 toilets on the roof.
all air handlers are floor standing units.
CENTRALIZED CONTROLLER AG-150
MA Remote Controller (PAR-21MAA) for each air handler.
Control 4 as a third party
8:00 am (12 hours after the set temperature changed from daytime 71 degrees up to night time 77 degrees and 1 hour before set to change back to daytime as we said before per the preset programming via Control 4.)
toilets exhaust fan has been turned off/ ERV is off
We took Relative Humidity Readings this morning and the following are our findings.
Readings at the follow locations:
Cellar front 76% back 68%
Basement front 70% back 68%
1st front 69% back 69%
2nd front 68% back 69%
3rd front 67% back 69%
4th front 69% back 69%
5th front 70% back 70%
Stair Bulkhead 72%
Stair hall 70% (consistently on most all floors)
Base point of the outside is:
Outside at front yard 76%
Last time we were taking readings, even with the toilet exhaust fan running, we measured 41% at 11 am after the systems scheduled changes.
Please advise because these seem like the changes in humidity could have ill effects on the many materials inside of the house.
we have a Mitsubishi Citi multi R-2 Series (heat recovery system) with BC controller, sub controller and (Lossnay) ERV system on the upper floor
3 fire places with FA.
Fresh air is introduced to the space thru the ERV system (as designed). I was told by the MC that the ERV is off.
One exhaust fan for 6 toilets on the roof.
all air handlers are floor standing units.
CENTRALIZED CONTROLLER AG-150
MA Remote Controller (PAR-21MAA) for each air handler.
Control 4 as a third party
8:00 am (12 hours after the set temperature changed from daytime 71 degrees up to night time 77 degrees and 1 hour before set to change back to daytime as we said before per the preset programming via Control 4.)
toilets exhaust fan has been turned off/ ERV is off
We took Relative Humidity Readings this morning and the following are our findings.
Readings at the follow locations:
Cellar front 76% back 68%
Basement front 70% back 68%
1st front 69% back 69%
2nd front 68% back 69%
3rd front 67% back 69%
4th front 69% back 69%
5th front 70% back 70%
Stair Bulkhead 72%
Stair hall 70% (consistently on most all floors)
Base point of the outside is:
Outside at front yard 76%
Last time we were taking readings, even with the toilet exhaust fan running, we measured 41% at 11 am after the systems scheduled changes.
Please advise because these seem like the changes in humidity could have ill effects on the many materials inside of the house.