I have in my plant a 2500 kW, 13200 V, 20 poles brushless synchronous motor. The machine was running and when it stopped i did the insulation test with 5 kV. The insulation test result was 3 MΩ. The machine is installed in sheltered place and it does not have any signs of oil, dirty or moisture. When we do the insulation test with the guard probe connected together with the ground probe, the result was 7 GΩ.
The machine is now running normally. Could someone explain me this phenomenon?