cry22
Mechanical
- May 15, 2008
- 448
I wonder, how much energy savings over ASHRAE 90.1 you guys are getting for office buildings in mderate climates?
In very cold climates we've been able to document as much as 58%.
Are you down sizing your chiller and boiler plants as a result of LEED? Do you remove some conservatism from your design because of LEED?
We have been able to get as much as 550 SF/ton for office buildings with Low-E glass and total energy recovery.
When we take away the descicant wheels, we have a hard time meeting the typcal mandate of ASHRAE 90.1 + 20%.
What is your experience and what are the LEED features you are implementing?
The following are the classics LEED features we implement:
1. Total energy wheels.
2. Air side economizers.
3. High efficiency condensing boilers.
4. Low-E glass, U=0.4, SC=0.3
5. DDC controls.
6. Low electrical loads (1 watt per SF for lighting)
7. 0.5 watts per SF for equipment.
8. dedicated 24-hour cooling systems (DX, dry coolers, etc) to shut down the chiller plant.
9. CO2 sensors for demand controlled ventilation.
The non-classics:
1. Geothermal energy.
2. Dynamic air filters, reducing static pressures by 1" on typical VAV systems.
What water saving features are you using? Have you implemented teh Dolphin water treatment system in lieu fo chemical treatment for cooling towers?
Hope to generate some contributions for all.
In very cold climates we've been able to document as much as 58%.
Are you down sizing your chiller and boiler plants as a result of LEED? Do you remove some conservatism from your design because of LEED?
We have been able to get as much as 550 SF/ton for office buildings with Low-E glass and total energy recovery.
When we take away the descicant wheels, we have a hard time meeting the typcal mandate of ASHRAE 90.1 + 20%.
What is your experience and what are the LEED features you are implementing?
The following are the classics LEED features we implement:
1. Total energy wheels.
2. Air side economizers.
3. High efficiency condensing boilers.
4. Low-E glass, U=0.4, SC=0.3
5. DDC controls.
6. Low electrical loads (1 watt per SF for lighting)
7. 0.5 watts per SF for equipment.
8. dedicated 24-hour cooling systems (DX, dry coolers, etc) to shut down the chiller plant.
9. CO2 sensors for demand controlled ventilation.
The non-classics:
1. Geothermal energy.
2. Dynamic air filters, reducing static pressures by 1" on typical VAV systems.
What water saving features are you using? Have you implemented teh Dolphin water treatment system in lieu fo chemical treatment for cooling towers?
Hope to generate some contributions for all.