Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

HVAC system shutdown - fire detection system 1

Status
Not open for further replies.

John_187

Mechanical
Apr 21, 2018
68
There is a project with VRFs, and dedicated outside air units. Is it typical for HVAC systems such as these to shut down in a fire event and interlock with the fire detection system? Thanks
 
Replies continue below

Recommended for you

Think about it, if it were not interlocked with the fire detection system, what would happen in the event of fire, particularly with the smoke?
 
This answer is always up for debate, and varies somewhat depending on where your project is (smoke detctor in supply duct or return duct, over 15,000 CFM detectors, etc).

I think you’ll find the following requirements.

If any of those systems are over 2,000 CFM (system being the combined CFM if it’s a shared space) - you need a duct smoke detector (could use area smoke if you want to meet the exception). And it is this detector that will shutdown the unit, when the unit is actually sensed to be spreading smoke. This sensing of smoke also needs to be communicated to the fire alarm control panel.

If you have a system at 15,000 CFM, then you need to go further and have smoke detectors at each floor branch - which would also shutdown the unit and communicate an alarm when smoke it sensed.

Practically speaking, anything that provides fresh air to the building would be better off being shutdown so the fire doesn’t keep getting oxygen. Anything exhausting the building, especially if it’s a dangerous or flammable, is probably better off staying on.

So final answer, if your VRFs are under 2,000 CFM, and incapable of spreading smoke beyond the enclosing walls, floors and ceilings of the room or space in which the smoke is generated - you should be able to leave them on. But turning them off is probably an improvement if it’s simple enough to implement. If the DOAS is over 2,000 CFM, it only has to shut off when it senses smoke, but if you can add functionality to the fire alarm to automatically shut it off, that is recommended.

It doesn’t mean it isn’t a good design practice to design the fire alarm system to shut down the HVAC systems when in alarm - I just have yet to see the part of the code where it directly states that the fire alarm system should be shutting down air handling units. The main exception to this is when the HVAC systems are also a smoke control system, then these would definitely need very specific control during a fire event.
 
In general, all HVAC equipment (that isn't smoke control) should be switched off in the fire zone where the fire is (for small buildings, that is usually the entire building). This is due to it being able to a) spread smoke, b) fan the fire (not nearly as important, since smoke kills people long before the fire does in most cases - in fact, most smoke exhaust systems will effectively fan the fire in any case, but the safe evacuation of people is much more important).

So, your fresh air system MUST be switched off. (unless it forms the make-up air for the smoke exhaust system)

The VRF system is up for a bit more debate - local regulations are usually vague and just mentions "all HVAC equipment" - in which case you either have to argue a relaxation (precedents can usually help you significantly here) or do it. If the local codes are more specific, then follow them.

I think that from a smoke management perspective, wall-mounted (or other room by room based VRF indoor units) are not critical to be switched off - but local codes dictate.

 
Status
Not open for further replies.

Part and Inventory Search

Sponsor