Hi everyone,
I would like someone's opinion on the secondary hydronic circuit approach that I have chosen for my design.
I have a heating system with a heat pump that serves as a heat generator (primary side) and it's decoupled from the secondary side by a buffer vessel. There are 4 secondary circuits, one of which requires lower flow temperature that the other circuits. Primary HP flow temp and three secondary circuits operate at 45C flow temp, while the fourth secondary circuit requires flow temp of 35C.
The secondary side is a pressurless circuit (no circulating pump between the buffer and the secondary circuits) and each secondary circuit has it's own VSD pump making them constant temperature, variable flow type circuits.
Based on my knowledge, there is just one way to set up the presurless, different temperature secondary circuit and that's via the three port mixing valve with premixing. This setup works and is recommended when the primary and secondary flow temps are different (in my case 45C and 35C respectively), and when the secondary side is a constant flow, variable temperature circuit.
My issue is that my secondary side is variable flow, constant temperature circuit and correct premixing is hard or impossible to achieve given it is a variable flow circuit. So, I have decided to go with a common mixing circuit (three port valve). Given it is a variable flow, constant temp circuit, this three port valve will always stay more or less open in a same position. It will always divert same amount of water through the bypass port. The part I'm unsure about is if this is a good solution from the control perspective? I know 3 port mixing valves are chosen and selected to work throughout the full openable range of valve, but this will not be the case in my setup.
Any thoughts?
I would like someone's opinion on the secondary hydronic circuit approach that I have chosen for my design.
I have a heating system with a heat pump that serves as a heat generator (primary side) and it's decoupled from the secondary side by a buffer vessel. There are 4 secondary circuits, one of which requires lower flow temperature that the other circuits. Primary HP flow temp and three secondary circuits operate at 45C flow temp, while the fourth secondary circuit requires flow temp of 35C.
The secondary side is a pressurless circuit (no circulating pump between the buffer and the secondary circuits) and each secondary circuit has it's own VSD pump making them constant temperature, variable flow type circuits.
Based on my knowledge, there is just one way to set up the presurless, different temperature secondary circuit and that's via the three port mixing valve with premixing. This setup works and is recommended when the primary and secondary flow temps are different (in my case 45C and 35C respectively), and when the secondary side is a constant flow, variable temperature circuit.
My issue is that my secondary side is variable flow, constant temperature circuit and correct premixing is hard or impossible to achieve given it is a variable flow circuit. So, I have decided to go with a common mixing circuit (three port valve). Given it is a variable flow, constant temp circuit, this three port valve will always stay more or less open in a same position. It will always divert same amount of water through the bypass port. The part I'm unsure about is if this is a good solution from the control perspective? I know 3 port mixing valves are chosen and selected to work throughout the full openable range of valve, but this will not be the case in my setup.
Any thoughts?