According to IEC 61892-3, manual speed control should be capable of a range from -20% to +10%. However, IEC 61892-1 specifies a manual speed control range of ±5%.

IEC 61892-3:
IEC 61892-3.JPG

IEC 61892-1:
IEC 61892-1.JPG
Are diesel engine set manufacturers able to comply with the requirements of IEC 61892-3?
 
Replies continue below

Recommended for you

Governor manufacturers are able to comply.
We had that feature on our small island utility generators.
Cat engines with Woodard governors.
The governors each had a small electric gear-motor that remotely adjusted the speed set-point.
You present twi issues;
1/ Is the governor capable of meeting the speed specs?
2/ Is a remote operation option available for the governor?
 
Governor manufacturers are able to comply.
We had that feature on our small island utility generators.
Cat engines with Woodard governors.
The governors each had a small electric gear-motor that remotely adjusted the speed set-point.
You present twi issues;
1/ Is the governor capable of meeting the speed specs?
2/ Is a remote operation option available for the governor?
The issue here , "Is the governor capable of meeting the speed specs?" as the Japanese manufacturer DAIHATSU say that IEC 61892 -3 requirement cannot be met, but can meet the classification society (ABS) standard. The installation is on a ship.
 