- Jul 14, 2021
- 7
Hi all,
I wanted to get some other opinions on the interpretation of the energy code economizer requirements. I am in Climate Zone 5, Chicagoland, for what its worth. IECC 403.5 requires economizers on systems over 54,000 btu/h cooling capacity. The second part of that requirement says
"The total supply capacity of all fan cooling units not provided with economizers shall not exceed 20 percent of the total supply capacity of all fan cooling units in the building or 300,000 Btu/h (88 kW), whichever is greater."
This statement essentially avoids a design using a bunch of individual systems, at 4-tons or less, totaling over 25 tons of capacity. But what if I have a building with a total cooling load of only 10 tons? Can I use two 5-ton systems without economizers because I am under the 300,000 Btu/h limit? or do ALL systems over 54,000 Btu/h require economizers regardless?
If I really wanted to avoid economizers, I could use three 3-ton systems and still satisfy the code. So, can I use two 5-ton systems without economizers?
Thanks
I wanted to get some other opinions on the interpretation of the energy code economizer requirements. I am in Climate Zone 5, Chicagoland, for what its worth. IECC 403.5 requires economizers on systems over 54,000 btu/h cooling capacity. The second part of that requirement says
"The total supply capacity of all fan cooling units not provided with economizers shall not exceed 20 percent of the total supply capacity of all fan cooling units in the building or 300,000 Btu/h (88 kW), whichever is greater."
This statement essentially avoids a design using a bunch of individual systems, at 4-tons or less, totaling over 25 tons of capacity. But what if I have a building with a total cooling load of only 10 tons? Can I use two 5-ton systems without economizers because I am under the 300,000 Btu/h limit? or do ALL systems over 54,000 Btu/h require economizers regardless?
If I really wanted to avoid economizers, I could use three 3-ton systems and still satisfy the code. So, can I use two 5-ton systems without economizers?
Thanks