Mohsin Jameel
Electrical
- Apr 22, 2021
- 2
In our plant We have MV 11KV power generation with NER of 40 Amps on each and 11/0.4 KV MV/LV trafo solidly grounded . We have earth grid through out our facility to sustain calculated short circuit current at each location. Have resistance of 2-5 ohm nearly at each point of 4sq KM facility for touch voltage and all equipment in site away from substation is directly connected to earth grid close to each equipment (donot have separate PE cable coming back to switchgear earth palte) and same earth grid of electrodes and cables network is connected to MV NER and LV trafo star point.
Want to clarify setting of earth relays for MV and LV motors outside in field, what percentage of Line-earth fault current should I consider in our case as return fault current is dependent on earth grid as no separate PE cable is available? Can we consider/name this arrangement as TT network? Should we need to install 300mA earth current setting for all motors to meet any standard requirement and limit touch potential?
Want to clarify setting of earth relays for MV and LV motors outside in field, what percentage of Line-earth fault current should I consider in our case as return fault current is dependent on earth grid as no separate PE cable is available? Can we consider/name this arrangement as TT network? Should we need to install 300mA earth current setting for all motors to meet any standard requirement and limit touch potential?