Is there such a thing as a transformer's MVA being increased past the ONAN rating without fans- such as making the radiators much larger?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
If we had asked for a self cooled 240 MVA transformer
Mbrooke said:Is there such a thing as a transformer's MVA being increased past the ONAN rating without fans- such as making the radiators much larger?
JASGripen said:Can the specs of the oil be changed to increase the MVA of the ONAN?
prc said:6) By using esters you can allow more oil rise. But still winding hot spot will be a limit unless you change winding insulation to Nomex from kraft paper. In reality designers take a lower current density so that even at ONAN the winding temperature gradient over oil will be modest, much less than 18K (78-60)