XR250
Structural
- Jan 30, 2013
- 5,956
I am working on a job where the contractor will be installing various angle iron ledgers on hollow 8" CMU walls. I am specifying 1/2"Ø Hilti HY70 screened anchors. What protocol are you guys using for the fabrication of the angles and installation? Drill 9/16"Ø holes in the angle iron, tack it up, mark the holes, take it down drill the 11/16"Ø holes in the CMU and install screen tubes, tack the ledger back up, squirt epoxy and then install the rods? What happens if the drill bit walks a little and the holes ends up slightly off?
Seems if you did it any other way, you would have to drill oversized holes in the angle iron for the screen tubes (would also have to cut the lip off the tube) and then have to weld plate washers on to bring them down to the correct diameter. That would also add a little eccentricity to the bolt.
Thoughts?
Seems if you did it any other way, you would have to drill oversized holes in the angle iron for the screen tubes (would also have to cut the lip off the tube) and then have to weld plate washers on to bring them down to the correct diameter. That would also add a little eccentricity to the bolt.
Thoughts?