aranoche
Petroleum
- Sep 29, 2013
- 5
Hi there,
I have problem at my instrumentation wiring from field to marshaling cabinets.
because of some trouble at detailed engineering, we should mix instruments that role as PCS and ESD to one JB with two multicable out. (of course it is out of client spec)
data i got are:
1. all instruments come out/in the JB are analogue, with same cable type.
2. two multipair cables out/in are each for ESD and PCS. (@ 12pair-1.5mm2)
3. there are two column of terminal blocks inside, one for ESD and one for PCS (@ 40 terminals)
attached is my wiring draft.
Is there any problem to system if i mixed this two?
regards,