Insulation under a low RC slab?
nivoo_boss
132
Hey everyone!
So I have to design a slab foundation for a loading dock shelter (light steel structure). It will be cast on gravel. My question is, should I put insulation under the slab? I’ve seen pictures like below where there is for example 100 mm of EPS under the slab. But since it does not reach out below the slab, it does not seem to help much in case of frost heaving – why use it then?
I’m thinking about ditching the insulation. The structure is light and the slab is on gravel which should not be too sensitive to frost heaving. And even if it is, some deformations here and there should not do much to the light and flexible steel structure that the slab is supporting.
What are your thoughts on the topic?
It appears this is on the exterior of the building?
If so, generally speaking that would be to prevent frost from affecting the building foundation more than protecting the slab itself. If your building foundation were frost-susceptible then this insulation could help prevent frost issues.
Yes, it's outside.
But how can it prevent frost issues? I mean, if the insulation does not reach beyond the foundation (about 1 m in the perimeter for example), then the ground below the insulation would still freeze and cause heaving - wouldn't it? Or do you mean that the insulation is elastic enough that the frost would compress the insulation a little when the soil below expands and the foundation would not move much?
Frost grows in a radial-ish pattern. So assuming the ground begins to freeze at the outside edge of the insulation, the theory is the frost wouldn't be able to penetrate all the way to the foundation. The thickness and length of the insulation is function of ambient temperatures and foundation depths. In your case, I'm skeptical of the amount of frost prevention provided by that detail. Since we know that the slab will be cleared all the time through the cold months, insulation only slows the penetration of the cold into the soils below. I do believe the intent is that some of the heat loss from the building will also help keep the frost at bay.
Do some research into frost-protected shallow foundations and that should turn up some stuff for you to chew on.