Gene M.
Mechanical
- Feb 14, 2020
- 4
A client has made a comment on a design to provide additional ductwork on a packaged rooftop unit to ensure the intake and exhaust are 10 feet apart. Currently the packaged unit has factory installed hoods which are on adjacent corners.
I'm aware of the 10-foot requirement between environmental air exhausts and mechanical air intakes under NYC Mechanical Code 501.3.1 (3) but it seems pretty implausible that literally every packaged rooftop unit in NYC was specified and installed in violation of code, and I want to say I was given a reason/exception for this situation but I can not find it. Is there a code citation or similar that justifies having intake and exhaust hoods on the same unit within the 10-foot (and 3-foot vertical) separation?
I'm aware of the 10-foot requirement between environmental air exhausts and mechanical air intakes under NYC Mechanical Code 501.3.1 (3) but it seems pretty implausible that literally every packaged rooftop unit in NYC was specified and installed in violation of code, and I want to say I was given a reason/exception for this situation but I can not find it. Is there a code citation or similar that justifies having intake and exhaust hoods on the same unit within the 10-foot (and 3-foot vertical) separation?