First, am I correct in believing that (3 pole) low voltage circuit breakers have both a 3 pole and single pole interrupting rating? If so...
Generally, are the interrupting ratings provided in technical literature for MCCBs, ICCBs, and LVPCBs and the like a 3 pole interrupting rating, and is not necessarily equal to the single pole rating? To me it seems like usually the only information provided about interrupting ratings are that they are symmetrical. Here's an example: (or google "eaton magnum ds" and click 4th result)
Do single pole interrupting ratings need to be considered for solidly grounded WYE systems? Said another way, do single pole interrupting ratings only need to be considered in systems where the line-ground voltage can be as high as the line-line voltage? It seems that it is only ever suggested to investigate the adequacy of the single pole rating in high resistance or corner grounded delta systems - for solidly grounded wye it seems most people simply check the 3 phase fault level and select a device with a high enough 'interrupting rating', as it is shown in the manufacturer's manuals.
Do they need to only be considered for slash rated, e.g. 480/277, devices or also for non-slash rated, e.g. 600 or 480.
Is it true to say that single pole interrupting ratings are generally not considered because it is assumed that the single line ground fault level will be sufficiently low? They are considered in 'special case' systems because a single pole may need to interrupt a line-line fault which is assumed not not be low magnitude?
NEC 110.9 applies to both single pole and 3 pole ratings, correct?
For spot networks with solidly grounded wye secondaries, should consideration be given to the single pole rating?
Unrelated to the above: Are network protectors simply breakers with a shunt trip and 32 relay or is there some other difference?
Generally, are the interrupting ratings provided in technical literature for MCCBs, ICCBs, and LVPCBs and the like a 3 pole interrupting rating, and is not necessarily equal to the single pole rating? To me it seems like usually the only information provided about interrupting ratings are that they are symmetrical. Here's an example: (or google "eaton magnum ds" and click 4th result)
Do single pole interrupting ratings need to be considered for solidly grounded WYE systems? Said another way, do single pole interrupting ratings only need to be considered in systems where the line-ground voltage can be as high as the line-line voltage? It seems that it is only ever suggested to investigate the adequacy of the single pole rating in high resistance or corner grounded delta systems - for solidly grounded wye it seems most people simply check the 3 phase fault level and select a device with a high enough 'interrupting rating', as it is shown in the manufacturer's manuals.
Do they need to only be considered for slash rated, e.g. 480/277, devices or also for non-slash rated, e.g. 600 or 480.
Is it true to say that single pole interrupting ratings are generally not considered because it is assumed that the single line ground fault level will be sufficiently low? They are considered in 'special case' systems because a single pole may need to interrupt a line-line fault which is assumed not not be low magnitude?
NEC 110.9 applies to both single pole and 3 pole ratings, correct?
For spot networks with solidly grounded wye secondaries, should consideration be given to the single pole rating?
Unrelated to the above: Are network protectors simply breakers with a shunt trip and 32 relay or is there some other difference?