Ingenuity
Structural
- May 17, 2001
- 2,356
Follow up on this closed thread: thread815-434353
ACI's Concrete International magazine (June 2019 issue) has a 6 page investigation paper entitled:
Available here for ACI members: Link
For those who do not have access to ACI and CI magazine here is a summary of the conclusions:
Bold added by me. Wow!
ACI's Concrete International magazine (June 2019 issue) has a 6 page investigation paper entitled:
Investigation of the Collapse of the Chirajara Bridge. A summary of a study conducted by members of ACI Committee 133, Disaster Reconnaissance.
Available here for ACI members: Link
For those who do not have access to ACI and CI magazine here is a summary of the conclusions:
Concrete International said:Conclusions:
In our opinion, the West Tower of the Chirajara Bridge collapsed because post-tensioned reinforcement placed in a slab meant to act as a tie between columns was insufficient by a large margin. In contrast, in the perpendicular direction (that is, in the direction of the deck), where no large stresses would have been expected, this slab tie (or tower slab) was provided with nine times more reinforcement. Had the provided reinforcement been rotated 90 degrees, the collapse would not have occurred.
Bold added by me. Wow!