Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations waross on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

IR TESTING DELTA CONNECTED MOTOR

Status
Not open for further replies.

ekuegler

Electrical
Jan 2, 2012
38
GB
Hi all,

Can someone please state the correct method to adopt in testing a delta connected 3 phase motors insulation resistance, & how it differs from testing a star connected 3 phase motor. We are having a dispute on the matter & an un-baised opinion would settle the argument.

Many thanks.

EK
 
Replies continue below

Recommended for you

There is absolutely no difference in procedure for performing standard insulation resistance test on complete winding of a wye or delta motor.

What is the difference that is suggested?

=====================================
(2B)+(2B)' ?
 
Thankyou electricpete,

The dispute was over how you complete an IR test, as stated it's identical for both Wye/delta. The opposing argument was that the delta configuration when tested needs splitting, not true as a low IR will be indicated regardless of doing so, only at the point of having established a low IR/if it were deemend necessary to prove which phase was dragging the IR down would it need splitting.

Best regards
 
The same would apply to a wye winding.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 
Yes that's correct, both would require splitting if it were ferments necessary to prove which phase was dragging the IR down, the dispute was that the delta configuration needed splitting regardless, which isn't the case.
 
As Pete says. Why the discussion?

Gunnar Englund
--------------------------------------
Half full - Half empty? I don't mind. It's what in it that counts.
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor

Back
Top