Grateful_A
Electrical
- May 18, 2019
- 1
Hello, curious what ya'll think.
The engineer on a project I am building is not requiring an equipment ground conductor to be installed with the control conduit for 4-20 mA twisted shielded pair cable to from the PLC to instruments. We'll tie the cable shield to ground at the PLC, but we will not have a separate equipment ground to ground the metallic conduit at either side of the run. This would honestly be the first time that I have not run an equipment ground in a control conduit to ground the conduit at each end to the enclosure/instrument.
Any thoughts on the removal of the equipment ground conductor in this particularly installation?
The engineer on a project I am building is not requiring an equipment ground conductor to be installed with the control conduit for 4-20 mA twisted shielded pair cable to from the PLC to instruments. We'll tie the cable shield to ground at the PLC, but we will not have a separate equipment ground to ground the metallic conduit at either side of the run. This would honestly be the first time that I have not run an equipment ground in a control conduit to ground the conduit at each end to the enclosure/instrument.