Is an Equipment Ground Conductor required for Instrument Control Conduits

Status
Not open for further replies.

Grateful_A

Electrical
May 18, 2019
1
Hello, curious what ya'll think.

The engineer on a project I am building is not requiring an equipment ground conductor to be installed with the control conduit for 4-20 mA twisted shielded pair cable to from the PLC to instruments. We'll tie the cable shield to ground at the PLC, but we will not have a separate equipment ground to ground the metallic conduit at either side of the run. This would honestly be the first time that I have not run an equipment ground in a control conduit to ground the conduit at each end to the enclosure/instrument.

Any thoughts on the removal of the equipment ground conductor in this particularly installation?
 
Replies continue below

Recommended for you

Maybe the drawings are showing comply with NEC bonding/grounding practices as a general note?
Is not the grounding/bonding of conduit/equipment cases/enclosure a code rule?
 
An equipment grounding conductor for 4-20 ma equipment is general practice in many industries and in many engineering standards.
However the Canadian Electrical Code does not generally require equipment grounding for class 1 and class 2 circuits.
The NEC is often very similar to the CEC.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 