Is it necessary to provide Key Maintenance Switch (Disconnection Switch) for FM200 system?
As per Clause 4.3.6 of NFPA 2001 (2018.ED), disconnection switch (key maintenance switch) shall be provided. However, the SPEC doesn't specify key maintenance switch even though the SPEC follows NFPA 2001. Besides, the material submittal and shop drawings have been approved without comments about key maintenance switch. Now when we are working on mock-up, the Consultant issues a comment to add key maintenance switch with code reference. As the Contractor, what should I do?
As per Clause 4.3.6 of NFPA 2001 (2018.ED), disconnection switch (key maintenance switch) shall be provided. However, the SPEC doesn't specify key maintenance switch even though the SPEC follows NFPA 2001. Besides, the material submittal and shop drawings have been approved without comments about key maintenance switch. Now when we are working on mock-up, the Consultant issues a comment to add key maintenance switch with code reference. As the Contractor, what should I do?