Hi All,
I understand it is good practice and will make fixing of reinforcing a great deal simpler on site, but is it really required (from any code point of view) to maintain spacing of reinforcing over a change in moment?
i.e. In a wall to wall corner I require 16mm bars horizontally @ 150 spacing (on the outside face). Still on the outside face but moving away from the corner I can comfortably change the spacing to 200 centers. There is a sharp drop in the moment. Is it ok to do this?
Thanks.