BSVBD
Structural
- Jul 23, 2015
- 463
What horizontal deflection criteria do you use for glass / windows?
IBC 2009, 2403.3 Framing. To be considered firmly supported, the framing members for each individual pane of glass shall be designed so the deflection of the edge of the glass perpendicu1ar to the glass pane shall not exceed L/175 of the glass edge length or 3/4 inch (19.1 mm), whichever is less, when subjected
to the larger of the positive or negative load where loads are combined as specified in Section 1605.
L/175??? I’ve always considered glass to be one of the more “brittle” materials that should require L/360 or L/600.
The Weyerhauser “U.S. Wall Guide” also recommends L/175, which, of course, is referenced back to IBC.
Here is what I’ve used in the past: (Please comment)
HORIZONTAL DEFLECTION CRITERIA
L/600 = Lat. wind on vertical element w/glass or brick
L/360 = Lat. wind on vertical element w/glass or brittle finish
L/240 = Lat. wind on vertical element w/semi- brittle finish
L/120 = Lat. wind on vertical element w/flexible finish
Thank you!
IBC 2009, 2403.3 Framing. To be considered firmly supported, the framing members for each individual pane of glass shall be designed so the deflection of the edge of the glass perpendicu1ar to the glass pane shall not exceed L/175 of the glass edge length or 3/4 inch (19.1 mm), whichever is less, when subjected
to the larger of the positive or negative load where loads are combined as specified in Section 1605.
L/175??? I’ve always considered glass to be one of the more “brittle” materials that should require L/360 or L/600.
The Weyerhauser “U.S. Wall Guide” also recommends L/175, which, of course, is referenced back to IBC.
Here is what I’ve used in the past: (Please comment)
HORIZONTAL DEFLECTION CRITERIA
L/600 = Lat. wind on vertical element w/glass or brick
L/360 = Lat. wind on vertical element w/glass or brittle finish
L/240 = Lat. wind on vertical element w/semi- brittle finish
L/120 = Lat. wind on vertical element w/flexible finish
Thank you!