Yassine.Stir
Electrical
Hello,
I started a new experience in a refinery and We are planning to change a pneumatic transmitter by smart transmitter which measures the level inside a Vessel.
After reading manuals and watching tutorials, I did the calculation and I found delta P at minimum level (0%) = -236 mbar and delta P at maximum level (100%) = -91 mbar. So I suggest to my collegues (the instrument technicians) to configure LRV as -236 and URV as -91 because the smart transmitter can accept the negative pressure but they didn't agree with me and they said that they have an old method: in fact, to eliminate the zero: they will consider LRV = 236 and URV = -91 - (-236) = 145 (span). I want to verify with you if someone has worked with this method before?
Thank you.
I started a new experience in a refinery and We are planning to change a pneumatic transmitter by smart transmitter which measures the level inside a Vessel.
After reading manuals and watching tutorials, I did the calculation and I found delta P at minimum level (0%) = -236 mbar and delta P at maximum level (100%) = -91 mbar. So I suggest to my collegues (the instrument technicians) to configure LRV as -236 and URV as -91 because the smart transmitter can accept the negative pressure but they didn't agree with me and they said that they have an old method: in fact, to eliminate the zero: they will consider LRV = 236 and URV = -91 - (-236) = 145 (span). I want to verify with you if someone has worked with this method before?