- Jun 7, 2021
- 3
The bottom tapping of the level bridle on hot oil vessel is connected to the suction line of the circulating pumps. When the pumps are not running both the trip transmitter and the indicating transmitter read approximately the same. When one of the pumps P321A/B/C is running this creates a reduced pressure in the level bridle which causes the level bridle and the level instrument to read approximately 9% low. When two of the pumps are running the error increases to approximately 18% (between trip and indicting transmitter).
change was made to the indicating transmitter bridle from another lower source (connect to drain line vessel) the issue still persist due to line clogging.(atteched sketch)
both option 1 and 2 not working with hot oil, to insure safety working level for the indicating transmitter 06-LT-3243.See attached
change was made to the indicating transmitter bridle from another lower source (connect to drain line vessel) the issue still persist due to line clogging.(atteched sketch)
both option 1 and 2 not working with hot oil, to insure safety working level for the indicating transmitter 06-LT-3243.See attached