Liquid Nitrogen store ventilation

Status
Not open for further replies.

ad77

Mechanical
Jan 26, 2003
22
AU
what is a typical ventilation arrangement for a store room housing liquid nitrogen vessels (small vessels associated with a laboratory)?

any assiatnce will be appreciated.
 
Replies continue below

Recommended for you

First thing is to check for existence of local codes. Nitrogen asphyxiation is very dangerous and it causes fatality, sometimes, without indication.

You should check with Dewar manufacturers about liquid N[sub]2[/sub]evaporation rates. 1 liter of liquid N[sub]2[/sub] evaporates into 24.6 ft[sup]3[/sup] of gas.

Generally. oxygen level should not be less than 18%. If I consider a typical evaporation rate of 0.095l/day/dewar then N[sub]2[/sub]gas released into the room will be 0.095*700 = 66.5 liters or 2.35 cu.ft/day. Suppose if your room size is 1000 cubic feet then oxygen content should be 209.5 cu.ft and nitrogen will be 790.5 cu.ft. But, due to asphyxiation N[sub]2[/sub] increases to 790.5+2.35 = 792.5 cu.ft and O[sub]2[/sub] will be 207.5 cu.ft or 20.75%. There is a reduction of 0.2% approximately. This type of calculation can be used to get required no. of fresh air changes in the absence of codes.

Oxygen monitor is a must IMHO. The following links will be useful to you.


Regards,
 
thank you imok & quark - as always, information that is relevant.
 
ad77, imok & quark,
I have made ventilation calculations using excel spreadsheet but it should be verified. The Liquid N2 freezer manufacturer rep never got back to me to let me know the evaporation rate. Also I am not sure if my procedure - calculating the critical concentration is correct. If you guys can give me your email address I can email you the spreadsheet & you can let me know what you think.
lilliput1
 
As Quark stated, “Oxygen monitor is a must IMHO.” I don’t know too much about the construction of a small Dewar; however, many large cryogenic storage vessels rely on maintaining a vacuum in the interstitial space. If there is a vacuum leak the evaporation rate will be much higher. Also, a oxygen sensor could monitor the area in case of a spill. One source that will have a lot of safety standards for this is the CGA (Compressed Gas Association.)
 
Lilliput,

If the transfer of liquid nitrogen is automatic by level control or temperature control inside the freezer then you have to only deal with evaporation rates resulting from temperature difference. But our application(storage of master cell banks) includes opening of cryocan lids. I never did the detailed calculation for evaporation when the lid is open because this includes evaporation of liquid nitrogen and superheating of gaseous nitrogen. We only take care of evaporation when the lid is closed and don't have much problems. O[sub]2[/sub] is in control.

I want to have a look at your spreadsheet. My id is builblock1@yahoo.com

PS: OSHA recommends oxygen level of 19.5%

Regards,


 