Load Calculation

Status
Not open for further replies.

zimmerDN

Electrical
Jan 17, 2013
34
I have a simple question about 3-phase supply with 1-phase loads.

If the supply is 3-phase 575V L-L and there are 1-phase loads.

10 A between phase A-B
10 A between phase B-C
10 A between phase A-C


What is the total load on each phase A, B, C? 10A or 20A?
 
Replies continue below

Recommended for you

The line current is sqrt(3) times the phase current, i.e. 17.3 amps.

An easy way to relate the line and phase current is this:
VLL = 575V
Iph = 10A
Zdelta = 575/10 = 57.5ohm
Zwye = Zdelta/3 = 19.1667ohm
VLG = 575/sqrt(3) = 331.976V
Iline = VLG/Zwye = 331.976/19.1667 = 17.3A

If you're curious about the angles, the line-line voltage leads the line-ground voltage by 30 degrees. Thus, the line current lags the phase current by 30 degrees.
 
I have to tell I have no sufficient imagination to understand how it is possible to measure the current between two phases.
If you have to supply a transformer connected in delta[triangle] or a resistor[for heating purpose] or even an induction motor with 6 conductors for
star-delta starting you never could measure current between phases directly but through an impedance[in series].All 6 winding ends have to be accessible [usually they are not] and put the ammeters in series.
It is correct to calculate the line current by multiplying the "between phases "current by 1.73 and the apparent power S=sqrt(3)*Iline*VoltL_L=3*IL_L*VL_L=3*10*575=17250 VA[17.25 kVA]
If you don't now the p.f.[cos(fi)]between supplied voltage and current produced you cannot calculate the active power P[w,kw or H.P.].
If the consumer [receiver] it is a pure resistance[let's say a heater formed from resistors] then p.f.=1 and then P=17.25 kw.
The ratio between voltage and current does not mean anything since, in case of a transformer, this will depends on the load and in the case of an induction motor it depends on speed [slip].
 
Time for a coffee break 7anoter4.
Loading on a transformer is much more meaningful expressed in VA or A than in Watts. There is enough information for either Ampere draw calculations or VA calculations.
We may assume equal PF for the loads until informed otherwise.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 