mrMikee
Structural
- Apr 23, 2005
- 528
I have a question about load combinations for use with allowable stress design and the application of the 0.75 factor for seismic loads when combined with live loads. Per sections ASCE 2.4.1 and IBC 1605.3.1:
Equation 6 in ASCE 7 is: D + 0.75L + 0.75(0.7E)
IBC Equation 16-10 is: D + L + 0.7E
The IBC goes on to say that the 0.75 factor can be applied to variable loads (wind and seismic) when combined with dead loads. My interpretation is that the IBC equation would become the same as the ASCE equation. However the IBC continues with "the 0.7 factor on E does not apply for this provision," but the commentary also says these reductions are similar to the ASCE. Does anyone know what the IBC is trying to say here?
Carrying this on to the next step brings me to section 1620.3.2 of the IBC concerning the direction of a seismic load where the 100%/30% rule is discussed. Using equation 6 from above (including the 0.75 factor) and assuming seismic loads are Ex and Ey I would get the following load combination:
D + 0.75L + 0.75(0.7Ex) + 0.225(0.7Ey)
Actually this load combination depending on the symmetry of the structure and applied loads could under certain condition result in a total of 8 equations.
Is there anything wrong with this logic?
Regards,
-Mike
Equation 6 in ASCE 7 is: D + 0.75L + 0.75(0.7E)
IBC Equation 16-10 is: D + L + 0.7E
The IBC goes on to say that the 0.75 factor can be applied to variable loads (wind and seismic) when combined with dead loads. My interpretation is that the IBC equation would become the same as the ASCE equation. However the IBC continues with "the 0.7 factor on E does not apply for this provision," but the commentary also says these reductions are similar to the ASCE. Does anyone know what the IBC is trying to say here?
Carrying this on to the next step brings me to section 1620.3.2 of the IBC concerning the direction of a seismic load where the 100%/30% rule is discussed. Using equation 6 from above (including the 0.75 factor) and assuming seismic loads are Ex and Ey I would get the following load combination:
D + 0.75L + 0.75(0.7Ex) + 0.225(0.7Ey)
Actually this load combination depending on the symmetry of the structure and applied loads could under certain condition result in a total of 8 equations.
Is there anything wrong with this logic?
Regards,
-Mike