Good Morning Everybody,
I am Michel. I have a question.
I am on a rig right now running 4 3516 engines with 600V Kato Generators.
I was running with 4 generators with Dual Exciter Coils and was able to load share perfectly.
Now I send one generator to be rewound and it returned with a Single Exciter Coil arrangement. I placed it in and we ran the load test on all engines.
Now below is what I see,
As we increase the load gradually from 0%, I see the load being shared equally, I am talking KW, KVA, Kvars.
As soon as I reach about 65% to 70%, I see the rewound generator not able to take more load,the amps, kva stands at its maximum point whereas the other 3 generators begin to share the increased load. I cant figure out the problem here because the system is designed to share the load equally.
I had taken the measurement of the exciter voltage at one point in between.
3 generators stood at 48 to 50V, whereas this particular rewound generator was at 82V.
Could you guide me as to where my problem lies, whether its to do with the coil arrangement or a bad coil or anything else?
Below is some info,
This generator details (#2 with single exciter coil) :
Model 1030-680361111
P/N 6p6-2700
1030KW- 1200 RPM-1240 AMP
Exciter field # 12090-42
Exciter ARM# 12058-42
Exciter volt 50/ 100
Exciter AMP 3.5/7
The other generators details (#1, #3 & #4 w/dual exciter coils) :
Model 1030-680361111
P/N 6p6-2700
1030KW -1200 RPM-1240 AMP
Exciter field # 12010-30
Exciter ARM# 12064-30
Exciter volt 100
Exciter AMP 2.7
Please do help, thank you.