Hello,
I am currently in a freaky trouble with the unknown reaction of the AVR-Engine Governor-and the actuator.
We are connected to the grid, with 5 step-up transformers, and each transformer is fed by 2 diesel generator(22.4MW) and engines are running in base mode, that means a power measuring relay 4-20mA output is going to governor, the governor also gets the power setpoint from PLC. With these two values, governor stabilise the power output of the engine. There is no load sharing or var sharing between each engines.
When 1 engine is running on 1 step-up there is no problem.
When we started two engines on same step-up, everything is going fine, after a day or 2 days, 2 engines that connected to the same transformer shutdown at the same time with the alarm "4-20mA failure" in governor. The reason is active power relay analog output is under 4 mA in reverse power so the governor determines this situation as 4-20mA. I just decrease the gain parameter of the governor of all engines, 8 engines are running fine but the engine 1 and 2 not. Load is swinging, also the fuel rack, and engine 1 and 2 shutdown.
All of the engines have the same settings and all of them are working fine except the engines 1 and 2.
You can see the picture as attachment;
-#1 for load swing and tripping #2 is excitation
I am currently in a freaky trouble with the unknown reaction of the AVR-Engine Governor-and the actuator.
We are connected to the grid, with 5 step-up transformers, and each transformer is fed by 2 diesel generator(22.4MW) and engines are running in base mode, that means a power measuring relay 4-20mA output is going to governor, the governor also gets the power setpoint from PLC. With these two values, governor stabilise the power output of the engine. There is no load sharing or var sharing between each engines.
When 1 engine is running on 1 step-up there is no problem.
When we started two engines on same step-up, everything is going fine, after a day or 2 days, 2 engines that connected to the same transformer shutdown at the same time with the alarm "4-20mA failure" in governor. The reason is active power relay analog output is under 4 mA in reverse power so the governor determines this situation as 4-20mA. I just decrease the gain parameter of the governor of all engines, 8 engines are running fine but the engine 1 and 2 not. Load is swinging, also the fuel rack, and engine 1 and 2 shutdown.
All of the engines have the same settings and all of them are working fine except the engines 1 and 2.
You can see the picture as attachment;
-#1 for load swing and tripping #2 is excitation