Hello, I a made a similar post of the below on the pump engineering forum, but got no replies.
We have a two pipe direct return cooling pipe system for a campus of buildings. Each building circuit is the secondary and the circuit between buildings is the primary. There are differing views as to whether the main balance valve for each building (secondary circuit) should be in the supply or return line.
1) One view is that for secondary circuits you place the balance valve on the supply. With the balance valve on the supply, it will be easier to set the flow into the building. (This is the perspective of the Test, Adjust, & Balance (TAB) technician from his experience.)
2) The other view is that having the balance valve on the return will reduce air and noise in the system.
1997 ASHRAE Fundamentals Handbook, page 33.4 says -- Compared with placement on the supply side, balance valves on the return side will reduce the amount of free air in the coil.
From ashrae above it is obvious that each individual coil should have the balance valve on the return. Would this also hold true for secondary circuits?
Is there any documentation stating that the balance valve for a secondary circuit should be placed on the supply?
We have a two pipe direct return cooling pipe system for a campus of buildings. Each building circuit is the secondary and the circuit between buildings is the primary. There are differing views as to whether the main balance valve for each building (secondary circuit) should be in the supply or return line.
1) One view is that for secondary circuits you place the balance valve on the supply. With the balance valve on the supply, it will be easier to set the flow into the building. (This is the perspective of the Test, Adjust, & Balance (TAB) technician from his experience.)
2) The other view is that having the balance valve on the return will reduce air and noise in the system.
1997 ASHRAE Fundamentals Handbook, page 33.4 says -- Compared with placement on the supply side, balance valves on the return side will reduce the amount of free air in the coil.
From ashrae above it is obvious that each individual coil should have the balance valve on the return. Would this also hold true for secondary circuits?
Is there any documentation stating that the balance valve for a secondary circuit should be placed on the supply?