Mbrooke
Electrical
- Nov 12, 2012
- 2,546
What are the typical choices of action when dealing with low SF6 and an SF6 cutout? Is an automatic relaying action initiated or is the decision left to operators via remote SCADA?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
davidbeach said:We get a steady stream of low gas alarms, all of which get attended to post haste. To my knowledge we've never had a breaker fail to trip due to the low-low block.
An automatic trip at low would be highly disruptive, possibly dropping load.
The switching necessary to isolate a breaker to add SF6 can be done without dropping load. Any breaker that goes from low to low-low faster than we can get gas added to it is probably loosing gas too fast to safely trip below the point at which it is no longer safe to allow the breaker to trip.
A clean breaker failure trip following a breaker at low-low having the trip blocked will be recovered from much quicker than the mess following a catastrophic breaker failure. Do what you will, but we'll continue to not trip on gas alarms.
Mbrooke said:Perhaps, but correct me if I am wrong. I am reading that even at near atmospheric SF6 levels a breaker can interrupt rated full load load. So provided the breaker is not opening a short circuit, no risk exists on tripping the breaker at low-low during a fast leak?
Mbrooke said:In the vast majority of cases all load serving substations are fed with at least 2 transmission sources,..
stevenal said:That may be true for pure SF6, but leaks work in two directions. At atmospheric pressure, you have a mixture of SF6, air, and water vapor. I would not be counting on it to interrupt.
Great policy, it makes maintenance so much easier. So how do we ensure the low low event doesn't occur during the time one source is out of service for maintenance?
marks1080 said:I'm used to the breaker tripping itself out for low-low SF6. What type of breaker are you using?
I'm thinking all of your discussions have been moot as the breaker will not wait for a trip signal on low-low SF6.
I suggest you really go through the breaker control circuit to see how it behaves on its own. It will trip itself. Above you mentioned that a breaker was 'allowed to go into low-low SF6 without tripping.' This is very confusing to me.
Has someone tampered with the internal breaker control cct to allow this? If not, you may want to look at buying different breakers.
Alarm on low SF6. Depending on voltage level you may want to move disconnect switches to really isolate the breaker (assuming you have MO disconnects) on low-low SF6.
It should also lock itself out.
Out of paranoia (or added security) you will often see these signals go into the relaying world. Any action to trip the breaker via protection will be redundant. Any 'block reclose' signal or supervision added into your reclosure scheme will be redundant. In my opinion you DO want to initiate breaker fail - though I've heard debates around this, I personally feel like breaker fail is required, especially when you already know that breaker is not healthy.
The discussion around being able to trip vs close a breaker should never occur at the same time. 'Tripping' is very different than 'opening' and totally different from 'closing.' Open and close commands to a breaker are operational procedures. Tripping is protection. Protection is what 99.9% of your attention should be focused on. A P&C engineer has to always make sure a breaker can trip during a fault.
marks1080 said:I know that these breakers are generally rated to open with low or no SF6 for load currents.
marks1080 said:There's actually a really good reason not to have a breaker fail protection send a trip into it's own breaker, and it has to do with making sure you don't leave your 125/250V DC signal on the trip coil, eventually cooking it to destruction.
Is not the same as this:slavag said:signal is send to breaker failure protection for zone fast tripping in case of fault on this feeder.
marks1080 said:In my opinion you DO want to initiate breaker fail - though I've heard debates around this, I personally feel like breaker fail is required, especially when you already know that breaker is not healthy.
which I would definitely not agree with.Mbrooke said:Perhaps, but correct me if I am wrong. I am reading that even at near atmospheric SF6 levels a breaker can interrupt rated full load load.