What are the typical choices of action when dealing with low SF6 and an SF6 cutout? Is an automatic relaying action initiated or is the decision left to operators via remote SCADA?
Follow along with the video below to see how to install our site as a web app on your home screen.
Note: This feature may not be available in some browsers.
marks1080 said:Hi Mbrooke,
I know that these breakers are generally rated to open with low or no SF6 for load currents. However, I personally think it would be a huge mistake to use this fact in operating decisions. If a breaker is known to have low-low SF6 it should be taken out of service and isolated immediately. Look at it from the point of view of how many possible contingencies away from catastrophic failure you are. If you don't isolate the breaker when you know its unhealthy how will it perform if exposed to some other system fault or condition? Treat the breaker as being 'failed' before it actually blows up. Initiate breaker fail on low-low gas and let the breaker fail protection clear the zone. Don't clear the zone if it's not necessary to do so. Do not modify the manufactures lock-out and trip logic. I'm fairly amazed those discussions are even taking place at your company.
Use the 'SF6 Low Gas Trip' contacts to initiate breaker fail. For these scenarios you need to rely on the breaker tripping itself. Sending signals via SCADA is an operational practice, nothing to do with protections. If you know your breaker is unhealthy (low-low SF6 for example) the fastest way to trip it (faster than BF or any other protection) is to let it trip itself. You are only a single contact operation away from picking up the trip coil then, so you trip speed is the speed of your motorized SF6 pressure switches plus one contact. If you trip via any other system you will add extra time to the trip action. You initiate breaker fail to take care of clearing the zone in the even that the breaker can't break the current, or for some other concurrent failure. Remember, when things go bad in primary equipment you can reasonably expect the chances for concurrent failures to go up.
For stage 1 low-SF6 you should alarm and dispatch. No need to take the breaker out of service immediately, although the dispatched workers who inspect the breaker would probably appreciate an outage. This can all be done via operator control, and no protection operation necessary.
If you know your breaker is unhealthy (low-low SF6 for example) the fastest way to trip it (faster than BF or any other protection) is to let it trip itself. You are only a single contact operation away from picking up the trip coil then, so you trip speed is the speed of your motorized SF6 pressure switches plus one contact.
One last point on Breaker Fail: I'm not sure but I got the impression from your above response that BF opens said breaker. This is not true. Breaker Fail does not try to trip it's own breaker, only the breakers in the adjacent zone. There's actually a really good reason not to have a breaker fail protection send a trip into it's own breaker, and it has to do with making sure you don't leave your 125/250V DC signal on the trip coil, eventually cooking it to destruction.
Frozen-E said:Are you suggesting that on top of having the breaker trip due to low gas, that the breaker fail protection clear the affected zone? That could get ugly pretty quickly.
marks1080 said:I can say that all the dead-tank SF6 breakers I've worked with (mitsubishi, siemens, abb) at the 115kV or higher level all trip themselves out on low-low gas. Avoiding this would require modifying the manufacturers wiring from what I've seen. It's kind like messing with an old oil breaker anti-pump or anti-slam scheme. You just wouldn't do it. Well not if you really understand the consequences of doing so.
marks1080 said:For your own information, my ABB 145PM63-20B breaker control cct has the 63-2 switch pick up a 63X1 relay for trip coil 1 and 63Z2 and 63Z1 relays in trip coil 2 (not sure why the add two relays here, maybe just spare contacts?). 63X1 will pick up trip coil 1 and 63Z2 picks up trip coil 2. 63X1 and 63Z2 are also used to supervise the close coil (block close). I'd upload a schematic, but honestly I'm not sure if it's proprietary or not. Either way you can probably imagine what I'm describing.