LV MCC Incomer sizing - 100% rated breaker

Status
Not open for further replies.

cherryg222

Electrical
Apr 6, 2016
23
We have a situation where the transformer (dry type) is rated at 1500/1770kVA (85/115degC). The secondary side current @ 480V for 1770kVA is 2129A. As per NEC Article 450.3(A), the secondary side OCPD needs to be sized at 125% of FLC i.e 2661A. If we choose to use 100% rated breaker (UL 1066 for Power CB supports 100% rated breakers), can we adopt a 2500A CB with 2500A bus, for the 480V MCC?
What is troubling me is that there is no exception to 450.3(A) with specific reference to 100% rated CBs.
 
Replies continue below

Recommended for you

I think you can definitely use 2500A rated CB.
The overload is always supposed to be for a limited time, hence need not be governing the continuous rating of ACB / busbars.
 
The 125% rule is the maximum. You can go smaller, depending on the calculated load on the MCC.

Bill
--------------------
"Why not the best?"
Jimmy Carter
 

Be aware that the breaker is tested by UL at 75degC terminals. If the feeder is designed with ampacity using conductor insulation such as THHN rated for 90oC, the breaker still needs to be selected for 125% or the feeder not to exceed 75oC.
 
Thanks all for your feedback. We are following the 75degC ampacities. Along with a 100% rated breaker and enclosure, we will be able to meet the requirement. I still had the question lurking for the bus of 2500A. I am guessing that the bus requires no derating and is good for continuous 2500A load based on temperature rise test.
 
Correct, bus in the MCC requires no de-rating.

But you seem solely focused on the conductors. Your TRANSFORMER is not rated to deliver 2500A continuously.


" We are all here on earth to help others; what on earth the others are here for I don't know." -- W. H. Auden
 
Jraef...My concern is upto 2129A only. Any current carrying part with any deration should be able to meet that amps. If the breaker is 100% rated in it's enclosure, and the bus bars are rated at 2500A and certified for it, everything will fall into place. We know that the design is 2x100% which would mean less than half the loading of the transformer during normal operation. My concern is the rating of 1770kVA should not have any unseen, hidden bottlenecks downstream.
 