cherryg222
Electrical
- Apr 6, 2016
- 23
We have a situation where the transformer (dry type) is rated at 1500/1770kVA (85/115degC). The secondary side current @ 480V for 1770kVA is 2129A. As per NEC Article 450.3(A), the secondary side OCPD needs to be sized at 125% of FLC i.e 2661A. If we choose to use 100% rated breaker (UL 1066 for Power CB supports 100% rated breakers), can we adopt a 2500A CB with 2500A bus, for the 480V MCC?
What is troubling me is that there is no exception to 450.3(A) with specific reference to 100% rated CBs.
What is troubling me is that there is no exception to 450.3(A) with specific reference to 100% rated CBs.