whycliffrussell

Electrical
Jul 10, 2006
92
For the purposes of short circuit calculations does anyone know if teck cable is considered 'magnetic duct' (due to the fact that it is encased in metallic armor)?
 
Replies continue below

Recommended for you

The type of raceway may not have significant impact in the SC rating of the cable. This mainly is a function of the insulation withstand temperature (initial & Max.), the conductor material and the duration of the SC (protective device tripping characteristics).

The enclose link will help to illustrate the SC effect on cable.

 
I'm not concerned about the SC rating of the cable in this case - I'm am modeling an existing system and am only concerned with how the magnetic duct effects the cable impedance and hence the downstream short circuit.
 
For practical purposes, resistance is unaffected by the conduit or armor material (magnetic or nonmagnetic). However, cable reactance may vary significantly if compared with single conductor cables installed in conduit. A rough approximation may be estimated as follow:
a) For nonmagnetic armor consider approx 20% less reactance than 3 single conductor in magnetic conduit.
b) For magnetic armor, consider approx 50% less reactance than 3 single conductor in magnetic conduit.
 