Greatone76
Structural
- Feb 2, 2006
- 64
I'm watching a contractor layout masonry dowels that go from the foundation into the masonry. I have standard 2 cell blocks. I want to see them layout the 16 inch lengths of the blocks then measure in 4 inches from the ends of the block to aim for the middle of the cells of the block. Using this layout method I have dowels that are more than 2 inches off that mark. I want to use the ACI 530 bar placement tolerance of +\-2 inch in the length of the wall to say that there layout doesn't meet the specs/code. I keep getting push back that as long as they end up in cells we are ok. I keep pointing out they are really tight to cell walls and some seem to me to be in the webs. I am aware of the 1/2 inch and 1/4 inch off the cells requirement based on grout, but I would like to see them in the middle as much as possible. Am I right to use my center of cell layout not meeting the spec or do I have to find 2 bars that are farther that the 2 inch tolerance and or rebar too close to cell walls? How do you apply the masonry spec in relation to masonry dowels?