- Nov 17, 2010
- 19
Hi all,
Curious to get opinions on the attached for max spacing of vertical bars, specifically clause AS3600 cl.11.7.3. and the 350mm requirement.
If the bars are staggered as per attached then max spacing between vertical 'parallel' bars is around 240 if they are spaced @ 400 on each face and offset diagonally. Would you consider this in accordance with the code or is the intent of the code for the bars each face to have a max spacing of 350mm?
Contractor is using a permanent formwork product which dictates bars at 200mm increments.
Thanks for your thoughts.
Regards
CRQUT
Curious to get opinions on the attached for max spacing of vertical bars, specifically clause AS3600 cl.11.7.3. and the 350mm requirement.
If the bars are staggered as per attached then max spacing between vertical 'parallel' bars is around 240 if they are spaced @ 400 on each face and offset diagonally. Would you consider this in accordance with the code or is the intent of the code for the bars each face to have a max spacing of 350mm?
Contractor is using a permanent formwork product which dictates bars at 200mm increments.
Thanks for your thoughts.
Regards
CRQUT