rterickson
Electrical
- Nov 15, 2001
- 114
The majority of our substation equipment was procured under ANSI standards in effect at the time of construction. Accordingly, our older 115 kV (nominal) disconnect switches, PT’s, circuit breakers, etc. are nameplated at 121 kV Rated Maximum Voltage. Since efforts in the mid-90’s to normalize ANSI standards with IEC, newer equipment is now marked 123 kV Maximum on the nameplate.
Since we typically operate at or below 120 kV, this is rarely an issue, but we have one distant switching station built in the 1950s that does see 122 kV under certain light load conditions. The Compliance folks are concerned about operating outside of ratings during these times.
The circuit breakers at this station were changed out in 2001, and we are adding new CVT’s later this year (planned end-of-life replacements). However the disconnects are still “good”, and likely run cooler than what we could purchase today.
It does not seem like a wise use of resources to replace all our switches to get new nameplates based on what seems like an arbitrary change in standards. Has anyone faced a situation like this? Is there any conceivable basis for rerating the switches?
Since we typically operate at or below 120 kV, this is rarely an issue, but we have one distant switching station built in the 1950s that does see 122 kV under certain light load conditions. The Compliance folks are concerned about operating outside of ratings during these times.
The circuit breakers at this station were changed out in 2001, and we are adding new CVT’s later this year (planned end-of-life replacements). However the disconnects are still “good”, and likely run cooler than what we could purchase today.
It does not seem like a wise use of resources to replace all our switches to get new nameplates based on what seems like an arbitrary change in standards. Has anyone faced a situation like this? Is there any conceivable basis for rerating the switches?