Continue to Site

Eng-Tips is the largest engineering community on the Internet

Intelligent Work Forums for Engineering Professionals

  • Congratulations IFRs on being selected by the Eng-Tips community for having the most helpful posts in the forums last week. Way to Go!

Medium Voltage switchgear panel fault

Status
Not open for further replies.

LMSANZ

Electrical
Jun 26, 2017
16
hi everyone,

we have under our facilities a 6kV swgr UNIGEAR ZS1, ABB made. Recently we had a fault in one of our motor starter panels (Fuse contactor VD4 type). The rear part of the contactor compartment is quite damaged.

In the same swgr we have a spare panel identical to the faulty one.

Cable length is not enough for re-connection to the spare panel. So I was wondering if is technically acceptable to prepare a 6kV cable (aprox 10m) for connecting the spare panel and use the cable compartment of the faulty panel as a junction box. All protections will be implemented in the new Spare panel of course.

Thanks

P1110194_tepf1o.jpg
 
Replies continue below

Recommended for you

I would prefair to pull the cable out of the Dameged panel and make a splice in cable room if possible
 
Status
Not open for further replies.

Part and Inventory Search

Sponsor