JacksonJim
split this into 2 issues
1. a cable was tested and there is debate around the voltage used..... more later
2. A cable was tested and
passed the test -
I am not keen on the voltage the test was done at
BUT IT PASSED and was good when the meter was disconnected.
-I hear "the you weakened it" argument but will say it survived at 5000V so it was good it did not slowly fade away overnight .
Look for something else - if you had carried out the insulation test for certifying it would hold true ... and the cert could be quoted in a disagreement.
I would suspect something else has happened and don't think you are the source of this particular evil.
for example
insulation knick at the gland entry,
the pressure point discribed earlier,
the nail gun fired nail we found in a 66KV cable run
and any one of a myriad of possibilties
the more later bit
Going forward ALWAYS get the manufacturers cable specs before stress testing -I know of cable which if marked 415/600V then 600 is the max rating and should not be tested higher
Go and find the manufacturers maximum rated voltage for testing -hopefully it will not be too bad
Having said that have a great day and smile
Don