Hi,

I've been asked to find an IEEE or equivalent test procedure for meggering from the T-leads in an MCC cubicle to the motor in the field. Any help would be much appreciated.

Ben
 
Replies continue below

Recommended for you

What is the operating voltage of your cables?

Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants
 
This is what I refer to when asked. There may be changes (Rev's) but pretty standard for Rotating Equipment and Cables. Corrections welcome.

IEEE STANDARD 43-1974 (29) ACCEPTANCE CRITERION FOR INSULATION
For Rotating Equipment
•IR is equal to or greater than 1 Megohm plus rated equipment KV.

MEGGER

IEE STANDARD NO. 43.1974
ACCEPTANCE CRITERION:
•IR IS EQUAL TO OR GREATER THAN 1 MEGOHM + RATED KV.

MOTOR RATING VOLTAGE DC MEGOHMETER (Test Voltage)
460/575 500 or 1000
2300/2400 1000 or 2500
4000/41602 2500
6600/6900 5000

POLARIZATION INDEX

PI = IR Measurement at 10 minutes
(Divided by)IR Measurement at 1 minute

ACCEPTANCE CRITERION:
Usually 2

IEEE STANDARDS: 690-1984(1), 422-1986(43), 43-1974 (29)
(for cable Insulation testing)

 
Again, I do not completely understand the application. However, I will give a warning that the IEEE standards noted are not applicable for shielded MV cables with extruded insulation. Per IEEE 400-2001 DC should not be used as it can damage aged cable and will not detect most defects. I recommend at least a AC withstand or, better yet, a PD stress test. Let me know if you have any questions.

Kind regards,

-Ben


Benjamin Lanz
Vice Chair of IEEE 400
Sr. Application Engineer
IMCORP- Power Cable Reliability Consultants
 