engrAlan
Structural
- Oct 9, 2012
- 21
Can anybody share any ideas as to what is the minimum embedment of a pedestal support.
We have fabricated a pre-cast concrete 300mm x 300mm x 600mm depth designed to support a 50kg instrument junction box. i did a calculation to determine the required embedment to the ground considering the lateral resistance of soil and is constrained on top with asphalt pavement.i used a calculation guide from IBC and it only requires 450mm embedment.
However,the site inspector insisted to use 600mm embedment based on their similar project. in this case we are 150mm less than his requirements. What will be the most suitable solution to our case?
Thank you.
We have fabricated a pre-cast concrete 300mm x 300mm x 600mm depth designed to support a 50kg instrument junction box. i did a calculation to determine the required embedment to the ground considering the lateral resistance of soil and is constrained on top with asphalt pavement.i used a calculation guide from IBC and it only requires 450mm embedment.
However,the site inspector insisted to use 600mm embedment based on their similar project. in this case we are 150mm less than his requirements. What will be the most suitable solution to our case?
Thank you.