Minimum rebar extension lengths in two way Post-Tensioned Flat System as per ACI 318!

Status
Not open for further replies.

AbhiCrux

Structural
May 8, 2014
3
Hi Fellow Engineers, I have a query on the above mentioned topic.

ACI 318-19, Fig. 8.7.4.1.3 shows the minimum extension lengths for two way (non-PT) flat slab system. (i.e., 0.33ln & 0.20 ln).

Would the same extension lengths apply for two-way PT Flat slab system? If no, can anyone help with the ACI clause suggesting about it. Design is being carried out in ADAPT Builder 2019!

Thanks in advance!!
 
Replies continue below

Recommended for you

Hi slickdeals!

8.7.5.5 applied for slabs with unbonded tendons. While I'm designing two way flat slab with bonded tendons. Anything for bonded tendons?

Thanks for the reply!
 