RangeRock
Structural
- Aug 2, 2021
- 22
Good Afternoon All,
Looking for some experiential wisdom regarding minimum reinforcing limits for a mass concrete design.
I am designing a reinforced concrete wall that is 3’-0”+ thick in most sections and is being poured indoors at an existing facility and will not be exposed to weather. However, it is being designed such that accelerated electron particles will not pass through the walls. Thus, I feel that the design exceeds the “liquid-tight” clause and is qualified as a “particle-tight” condition under ACI 350-06: 7.12.2.1.
Can I use the provision in ACI 350-06: 7.12.2.1 to reduce the shrinkage and temperature ratio to .0050 for the top and bottom 12” layers as described? Or am I required to stick with ACI 318-14: Table 11.6.1 with the prescribed reinforcement ratios as a function of total area?
Thanks in advance for the wisdom.
Looking for some experiential wisdom regarding minimum reinforcing limits for a mass concrete design.
I am designing a reinforced concrete wall that is 3’-0”+ thick in most sections and is being poured indoors at an existing facility and will not be exposed to weather. However, it is being designed such that accelerated electron particles will not pass through the walls. Thus, I feel that the design exceeds the “liquid-tight” clause and is qualified as a “particle-tight” condition under ACI 350-06: 7.12.2.1.