waterppk
Mechanical
- Jul 27, 2020
- 2
I'm working on a mixed use building for a non-profit organization. We're looking to install a caretaker's quarters for a building manager and trying to navigate code. The building is 2 stories, 9600 sq ft per floor plate, 600 sq ft on the 2nd floor will be the caretaker's space (residential), the rest of the building is IIIB construction with business occupancy.
The code question I'm trying to figure out:
Is it possible to provide a NFPA 13D sprinkler system for just the caretaker's quarters without sprinkling the entire building?
What I've found for documentation:
***
IBC section 903.2.8 Group R Section 903.3, requires a sprinkler throughout the building
but what's confusing
2015 IBC Table 508.4:
B, F-1, M, and S-1 needs a 2 hour separation from R when non-sprinkled, 1 hour with sprinklers
***
Why does table 508.4 provide a sprinkled and non-sprinkled separation if 903.2.8 requires sprinklers throughout? What would be the instance when 508.4 would have a non-sprinkled B, F-1, M, or S-1 occupancy adjacent to a R occupancy?
Thank you for any clarification you can offer! We'll likely sprinkle the whole structure, but I'd still like to understand how the code is meant to be used/interpreted.
The code question I'm trying to figure out:
Is it possible to provide a NFPA 13D sprinkler system for just the caretaker's quarters without sprinkling the entire building?
What I've found for documentation:
***
IBC section 903.2.8 Group R Section 903.3, requires a sprinkler throughout the building
but what's confusing
2015 IBC Table 508.4:
B, F-1, M, and S-1 needs a 2 hour separation from R when non-sprinkled, 1 hour with sprinklers
***
Why does table 508.4 provide a sprinkled and non-sprinkled separation if 903.2.8 requires sprinklers throughout? What would be the instance when 508.4 would have a non-sprinkled B, F-1, M, or S-1 occupancy adjacent to a R occupancy?
Thank you for any clarification you can offer! We'll likely sprinkle the whole structure, but I'd still like to understand how the code is meant to be used/interpreted.