I am involved in a project that is currently in the construction phase. While out in the field and inspecting some of the moment connection welds, we noticed several instances where several of the shear tabs were welded off to the beams. These beams are cantilevered and moment connected. When asked why several of these pieces were welded off in addition to the bolts, the contractor said the welds were done to level/plumb the steel. The connection in question is to the right of the uploaded picture. AISC 13th edition, Section 16 Chapter J1.8 states that "in such connections the available strength of the bolts shall not be taken as greater than 50 percent of the available strength of bearing-type bolts in the connection". If this is the case, would this mean that the weld would essentially need to be designed to take the full shear capacity of the connection? We have asked for the contractor to remove the welds, but worry that if they burn/grind too much that the beam web may be damaged. Any opinions for a course of action?
Thank you