Let me begin with my present situation; I have a Chinese built system which employs a Schneider Electric Magelis touchscreen HMI control unit and 3 Variable frequency drives .37kW Danfoss 132F0002 ( One of my frequency drives have failed and the control unit is showing a modbus error (in chinese).
The drives receive a start command from another PLC (Siemens S7 200CN, via Relay Output card) however there is no wired speed reference, so the speed reference set-points of the drives come from the Magelis HMI control unit via RS-485 (2 wire). I am in possession of a Danfoss LCP 11 programming interface.
My understanding of the system leads me to believe that each drive will have a separate address and a replacement drive will have to be programmed with the correct address in order to function properly.
My question is this: How do i go about determining the address of the defective drive? (connecting the LCP 11 yields no result as drive is damaged)
I am aware that some sort of capture may need to be done of the RS-485 data to see what addresses commands are being sent to and assign one of the 3 addresses used to the replacement drive in a process of trial and error.
I am grateful for any possible assistance.
Let me begin with my present situation; I have a Chinese built system which employs a Schneider Electric Magelis touchscreen HMI control unit and 3 Variable frequency drives .37kW Danfoss 132F0002 ( One of my frequency drives have failed and the control unit is showing a modbus error (in chinese).
The drives receive a start command from another PLC (Siemens S7 200CN, via Relay Output card) however there is no wired speed reference, so the speed reference set-points of the drives come from the Magelis HMI control unit via RS-485 (2 wire). I am in possession of a Danfoss LCP 11 programming interface.
My understanding of the system leads me to believe that each drive will have a separate address and a replacement drive will have to be programmed with the correct address in order to function properly.
My question is this: How do i go about determining the address of the defective drive? (connecting the LCP 11 yields no result as drive is damaged)
I am aware that some sort of capture may need to be done of the RS-485 data to see what addresses commands are being sent to and assign one of the 3 addresses used to the replacement drive in a process of trial and error.
I am grateful for any possible assistance.