Good day to all. I did a cable sizing calculation to determine the appropriate power conductor size for a 3phase, 480VAC motor feeder conductor based from
a)Ampacity (to consider conductor de-ration)
b)Steady State Voltage Drop (based from an allowable 3% Vdrop)
c)Motor Starting Voltage Drop (based from a modest 10% conductor Vdrop)
d)Short circuit thermal withstand capability (based from ICEA conductor thermal equation with the available 480VAC 3phase fault at a portion of the cable calculated with acceptable accuracy and the MCP clearing time specified.
Just when I thought the calculation was appropriate, I was directed not to consider item d) since they do not normally include it on LV conductor sizing. Is this code wise appropriate? The CEC code also take reference to this ICEA thermal equation as well…is this supposed to be an optional check and depends on client’s preference or is this one of those situations where a compromise has to be taken?
I was always under the impression that the conductor should be able to withstand the momentary fault within the OCPD clearing time.
a)Ampacity (to consider conductor de-ration)
b)Steady State Voltage Drop (based from an allowable 3% Vdrop)
c)Motor Starting Voltage Drop (based from a modest 10% conductor Vdrop)
d)Short circuit thermal withstand capability (based from ICEA conductor thermal equation with the available 480VAC 3phase fault at a portion of the cable calculated with acceptable accuracy and the MCP clearing time specified.
Just when I thought the calculation was appropriate, I was directed not to consider item d) since they do not normally include it on LV conductor sizing. Is this code wise appropriate? The CEC code also take reference to this ICEA thermal equation as well…is this supposed to be an optional check and depends on client’s preference or is this one of those situations where a compromise has to be taken?
I was always under the impression that the conductor should be able to withstand the momentary fault within the OCPD clearing time.