By the increasing insulation option I'm guessing that the motor could just be used on a larger load for example and would draw more current as demenaded by that load, and because the insulation is rated highher the motor can now withstand this current increase required by the load. The rotor remains unaffected.
Correct. No change in torque speed characteristics with the option where we use improved insulation (thinner or higher temperature rating). If you didn't change the characteristics of the fan or pump, you'd be at the same operating point. Presumably there must be a new load connected to draw increased load at same speed. Otherwise there is no change (unless we increase motor speed.... a different option).
By decreasing the stator turns option and thus decreasing flux density I'm guessing that there is more current due to the fact there is a lesser overall impedance in the stator. Less impedance will equal more current, and it is this current that will be used to provide more torque and hp.
For one thing, decreasing turns actually increases the flux density (flux depends on volts per turn) which does increase the torque speed curve. We will operate at lower slip for a given load As far as the rest I have to step back and think. This has a variety of effects.
Bad effects:
* It costs more magnetizing current and more core loss, both of which hurt the thermal performance of the stator.
Good effects:
* Since rotor power factor angle doesn't change, we can extract a little more torque per rotor current (torque would be proportional to rotor current times flux density times a power factor angle related to power factor of the rotor). So we reduce I^2*R heating in the rotor for a given power levle. But we have altered the "turns" ratio between rotor current and stator current, so we don't save anything on stator load component current. But reduced heat production in rotor can help the stator thermal performance.
*If we have eliminated 10% of series stator turns, then we can afford to make stator conductors 10% larger areawise which will reduce I^2*R losses
Both of the above good thermal effects (to the extent they exceed the bad thermal effects) recduce heating for a given load level and allow us to push a little more without exceeding thermal limits.
Also increasing the torque speed curve can be a good thing in terms of less heating during start for both rotor and stator.
=====================================