Hi,
Could you please help me on understanding the wiring of Motor winding and Bearing RTDs?
We have 250kW ID fan motor with 6 nos. of Winding PT100 RTDs. 2 Nos. of Bearing RTDs.
My MCC supplier has provided only 3 Terminals (2 + 1 shield) per RTD at at VFD. I have checked my previous projects and found that they had 4 Terminals (3 + 1 shield) for RTD wiring. Now, my Question is, is it enough to go with 3 Terminals (2+1shield) for RTD wiring at VFD? I have purchased Triad cable for this purpose. How Can I overcome this issue?
Thanks.
Could you please help me on understanding the wiring of Motor winding and Bearing RTDs?
We have 250kW ID fan motor with 6 nos. of Winding PT100 RTDs. 2 Nos. of Bearing RTDs.
My MCC supplier has provided only 3 Terminals (2 + 1 shield) per RTD at at VFD. I have checked my previous projects and found that they had 4 Terminals (3 + 1 shield) for RTD wiring. Now, my Question is, is it enough to go with 3 Terminals (2+1shield) for RTD wiring at VFD? I have purchased Triad cable for this purpose. How Can I overcome this issue?