bacon4life
Electrical
- Feb 4, 2004
- 1,498
I am purchasing a new 115/15 kV mobile substation and would like to check on the best way to provide reliable pump motor operation over a wide voltage range. Due to various different nominal distribution voltages, the 120/208 station service transformer voltages will range from 100V to 125V.
Can I just oversize the pump and fan motors by (115/100)^2 = 33% to account for the reduced torque at the lower voltage? Would that also give an acceptable margin for over excitation cooling at 125V? Each three phase motor will be in the 0.25 to 5 hp range.
I could also put in a boost transformer with a selector switch for each nominal voltage. However, I would like to Keep It Simple since installing the mobile is sometimes a rush job in the middle of the night.
Any other options I should consider?
Thanks,
Mark
Can I just oversize the pump and fan motors by (115/100)^2 = 33% to account for the reduced torque at the lower voltage? Would that also give an acceptable margin for over excitation cooling at 125V? Each three phase motor will be in the 0.25 to 5 hp range.
I could also put in a boost transformer with a selector switch for each nominal voltage. However, I would like to Keep It Simple since installing the mobile is sometimes a rush job in the middle of the night.
Any other options I should consider?
Thanks,
Mark