We have had a problem at a sanitary lift station and would appreciate any comments or suggestions.
The station is equipped with two (2) 28.2 HP (21.0 kw)submersible pumps and a 80 kw diesel generator with an 200A automatic transfer switch. The generator is sized ot operate two motors on a staggered start sequence.
The pumps operate fine when connected to utility power. When the pumps are operated via the stand by generator, the across line motor starter will "chatter" briefly (less than 1 second).
The submersible pump motor has a full load amp rating of 32.3 amps at 480 volts, and operates at 3450 RPM. The published locked rotor current for the motor is 245 amps. The NEMA code rating for the motor is "H".
During operation from the utility power, the in rush current has been measured between 380 amps and 420 amps (depending on leg and test). This was measured with a Fluke model 453(?).
When the generator attempts to start one of the pump motors, the control voltage will drop from 120 volts to ~ 75 volts. The control transformer is 5 kva. Two different transformers have been installed, with the second unit incorporating taps to try to provide some adjustment. The only items requiring control power at this point are the coils of the motor starter. There have been two different manufacturers of motor starters installed in the control panel
The submersible pump manufacturer states that the inrush current is with in an acceptable limit of 10 to 15 times FLA. They also state that since the units operate on utility power the issue is with the gen set.
The generator has had the voltage regulator changed, and the voltage has been adjusted to provide between 460 volts to 502 volts. The same results have occured. During the last round of testing , one of the units stopped "chattering", but the other unit has not (for no apparent reason or adjustment).
We would appreciate any type of response as we are currently baffled.
The station is equipped with two (2) 28.2 HP (21.0 kw)submersible pumps and a 80 kw diesel generator with an 200A automatic transfer switch. The generator is sized ot operate two motors on a staggered start sequence.
The pumps operate fine when connected to utility power. When the pumps are operated via the stand by generator, the across line motor starter will "chatter" briefly (less than 1 second).
The submersible pump motor has a full load amp rating of 32.3 amps at 480 volts, and operates at 3450 RPM. The published locked rotor current for the motor is 245 amps. The NEMA code rating for the motor is "H".
During operation from the utility power, the in rush current has been measured between 380 amps and 420 amps (depending on leg and test). This was measured with a Fluke model 453(?).
When the generator attempts to start one of the pump motors, the control voltage will drop from 120 volts to ~ 75 volts. The control transformer is 5 kva. Two different transformers have been installed, with the second unit incorporating taps to try to provide some adjustment. The only items requiring control power at this point are the coils of the motor starter. There have been two different manufacturers of motor starters installed in the control panel
The submersible pump manufacturer states that the inrush current is with in an acceptable limit of 10 to 15 times FLA. They also state that since the units operate on utility power the issue is with the gen set.
The generator has had the voltage regulator changed, and the voltage has been adjusted to provide between 460 volts to 502 volts. The same results have occured. During the last round of testing , one of the units stopped "chattering", but the other unit has not (for no apparent reason or adjustment).
We would appreciate any type of response as we are currently baffled.